Advantech Webaccess 与SIMENS S7-400PLC的连接设置

Advantech Webaccess 与SIMENS S7-400PLC的连接设置

Advantech Webaccess SIMENS S7-400PLC的连接设置

月初在深圳大亚湾核电站测试Advantech Webaccess与西门子S7-400的PLC连接测试,在测试中因为手头只有Advantech Webaccess与S7-300的连接测试文档,按照此文档设置,一直连接不通,最后再仔细研究Advantech Webaccess与S7-300的连接测试文档,发现在与S7-300的连接的文档中,其中一项是TSAP in Hex :Device ID, RackSlot: 03.02,如图:


在西门子的集成商的帮助下,RackSlot03.0202代表是CPU的槽位,即:S7-300的的CPU槽位在第二槽,而现场的S7-400CPU槽位在第三槽,所以将TSAP in Hex :Device ID, RackSlot设置为: 03.03,如图:



设置完成后可通讯。

[ 本帖最后由 XDL 于 2013-3-22 09:48 编辑 ]
Attachment: Your usergroup does not have permission to access attachments

TOP

PlC S7400H- Adam3600

Hi dearIn my project S7400H first link TSAP in Hex is 03.05
Bust PLC redundant link in Rack 1 can not connect to adam3600.
Plc1: rack 0 , Slot 5 :    connect with 03.05
PLC2: rack 1  slot 5 : can't connect.
I tested : 03.05 - 05.05 - 03.0F - 06.0F  - 03.03

Could you help me?

TOP